Hello,
I am currently troubleshooting a DT800 with multiple analog and digital sensors connected to it to monitor a residence. The analog sensors in question are several thermocouples and a RH sensor.
The issue we have is that the datalogger will report unreasonably high 15 min. data for several of the sensors simultaneously and then go back after an hour or so (sometimes randomly) to reporting normal readings. The digital channels are not affected, however, the analog channels that are affected are not consistent form day to day. This issue does not occur diurnally and seems to only correlate with with higher temperatures.
We did review our grounding for the sensors and have installed only the shielded cable grounds to the chassis ground. We also installed and instrument isolation transformer in between the grid and logger power supply as well as the RH sensor reference power supply.
Any thoughts on this would be greatly appreciated.
Thanks,
Matt