Network configuration

I can't get connection to my DT800 using Ethernet. In profile I've set the static IP for logger gateway and so on (when that is done a message of resetting logger appears, and the logger resets).

I can ping the logger but when i connect via Ethernet. I don't remember the words but in the log i get a message like "connection was force rejected" or something. Just wondering what IP is set under connection/properties/network? (where i can put IP and a gateway).

I can't get connection to my DT800 using Ethernet. In profile I've set the static IP for logger gateway and so on (when that is done a message of resetting logger appears, and the logger resets). I can ping the logger but when i connect via Ethernet. I don't remember the words but in the log i get a message like "connection was force rejected" or something. Just wondering what IP is set under connection/properties/network? (where i can put IP and a gateway).

Good morning Sushi,

We will need to know the exact error message. Also check the port number in the connection definition, for DT800 it needs to be port 8. And check that port 8 is not being blocked by any firewall.

Cheers,
Roger

Good morning Sushi, We will need to know the exact error message. Also check the port number in the connection definition, for DT800 it needs to be port 8. And check that port 8 is not being blocked by any firewall. Cheers, Roger