Let us know
Calculating Evapotranspiration

Our distributor in Chile sent us a request to implement PenMan-Montieth formula for evapotranspiration measurement using dataTaker. This formula requires several parameters that need to be calculated first from 10 measurements:

  • temperature (average, maximum and minimum)
  • relative humidity (average, maximum and minimum)
  • wind speed average
  • radiation
  • altitude from sea level
  • latitude

We manage to develop such script within dataTaker for this calculation, I have already included sensor information as well. You may replace the sensor with other brand as required. This is the script:

BEGIN"EVAPTR"
PROFILE HOST_PORT BPS=4800
PROFILE HOST_PORT FUNCTION=SERIAL
PROFILE SERSEN_PORT BPS=9600
PROFILE SERSEN_PORT DATA_BITS=8
PROFILE SERSEN_PORT PARITY=NONE
PROFILE SERSEN_PORT FLOW=NONE
PROFILE SERSEN_PORT MODE=RS422
PROFILE SERSEN_PORT FUNCTION=MODBUS_MASTER

S1=0,4000,0,56

RS1M

RA1M
'reading parameters
'Thies Clima US 4.9200.00.001: MODBUS RTU
1MODBUS(AD1,R3:5005,MBL,MES,"T~degC",0.1,=101CV,W)
102CV(W)=101CV
1MODBUS(AD1,R3:5013,MBL,MES,"RH~%",0.1,=103CV,W)
104CV(W)=103CV
1MODBUS(AD1,R3:5001,MBL,MES,"WS~m/s",0.1,=105CV,W)
106CV(W)=105CV

'Kipp and Zonen CMP10: terminal 1+ and 1-
1V(S4,=107CV,W)
108CV(W)=107CV

'normal weather measurement every 15 minutes
RB15M LOGONB
101CV(AV,"T~degC")(MX,"T Max~degC")(MN,"T Min~degC")
103CV(AV,"RH~%")(MX,"RH Max~%")(MN,"RH Min~%")
105CV(W)(AV,"WS_AV~m/s")


'evapotranspiration calculation every day
RC1D LOGONC
102CV(W)(AV,=1CV)(MX,=2CV)(MN,=3CV)
104CV(W)(AV,=4CV)(MX,=5CV)(MN,=6CV)
106CV(W)(AV,=7CV)
108CV(W)(AV,=8CV)

'Garmin 18x PC: HOST port
2SERIAL("\m[GPGGA,]\m[,]%2d[201CV]%f[202CV]\m[,]\m[,]\m[,]\m[,]\m[,]\m[,]\m[,]%f[9CV]\e")
9CV("Altitude~masl")=66
10CV("Latitude~deg")=201CV+(202CV/60)

'Date
20SV("Date",=51CV)
21SV("Month",=52CV)
22SV("Year",=53CV)

'calculation
11CV("Latitude~rad",FF2)=D2R(10CV)
12CV("Atmospheric Pressure~kPa",FF2)=101.3*((293-0.0065*9CV)/293)^5.26
13CV("Latent Heat~MJ/kg",FF2)=2.501-(2.361*3CV/1000)
14CV("Psychrometric Constant~kPa/degC",FF2)=(1.013/(1000*0.622))*12CV/13CV
15CV("Vapour Pressure T~kPa",FF2)=0.6108*E^(17.27*1CV/(1CV+237.3))
16CV("Vapour Pressure T max~kPa",FF2)=0.6108*E^(17.27*2CV/(2CV+237.3))
17CV("Vapour Pressure T min~kPa",FF2)=0.6108*E^(17.27*3CV/(3CV+237.3))
18CV("Average Vapour Pressure~kPa",FF2)=(16CV+17CV)/2
19CV("Vapour Pressure Saturation Slope~ kPa/degC",FF2)=4098*15CV/(1CV+237.3)^2
20CV("Mod Psychrometric Constant~kPa/degC",FF2)=14CV*(1+0.34*7CV)
21CV("Actual Vapour Pressure~kPa",FF2)=(0.5*17CV*5CV/100)+(0.5*16CV*6CV/100)
22CV("Aerodinamic Term for PM~mm/day",FF2)=(20CV*900*7CV*(18CV-21CV))/((19CV+20CV)*(1CV+273.16))

1IV(W)=(275*52CV/9)
2IV(W)=(9+52CV)/12)
3IV(W)=(53CV/4)
4IV(W)=(53CV+2-4*3IV)/3
23CV("No of Days in Julian calendar")=1IV-(2IV*(1-4IV))+51CV-30
24CV("Inv Relative Distance to the Sun~rad",FF2)=1+0.033*COS(2*PI*23CV/365)
25CV("Solar Declination~rad",FF2)=0.409*SIN(2*PI*23CV/365-1.39)
26CV("Solar Declination Angle~rad",FF2)=ACOS(-TAN(11CV)*TAN(25CV))
27CV("Extraterrestrial Radiation~MJ/m2",FF2)=(118.08/PI)*24CV*(26CV*SIN(11CV)*SIN(25CV)+COS(11CV)*COS(25CV)*SIN(26CV))
28CV("Solar Radiation~MJ/m2",FF2)=8CV*0.0864
29CV("Net Solar Radiation~MJ/m2",FF2)=(1-0.23)*28CV
30CV("Solar Radiation on clear sky~MJ/m2",FF2)=(0.75+2*10^-5*9CV)*27CV

31CV("Net Wave Radiation~MJ/m2",FF2)=4.903*(10^-9)*((2CV+273.16)^4+(3CV+273.16)^4)*(0.34-0.14*SQRT(21CV))*(1.35*(28CV/30CV)-0.35)/2
32CV("Net Radiation~MJ/m2",FF2)=29CV-31CV
33CV("Radiation Term~mm/day",FF2)=0.408*19CV*32CV/(19CV+20CV)
34CV(W)=33CV+22CV
34CV("Evapotranspiration~mm/day",FF2)=(34CV<0)?0:34CV
END

That script has 3 schedules:

  • schedule A that running every minute to read weather sensors.
  • schedule B that run every 15 minutes to calculate statistic from schedule A
  • schedule C that run every day to calculate evapotranspiration.

Evapotranspiration itself will be calculated on daily basis using statistic of 1 minute measurement.

Best regards,
Rudy Gunawan

Our distributor in Chile sent us a request to implement PenMan-Montieth formula for evapotranspiration measurement using dataTaker. This formula requires several parameters that need to be calculated first from 10 measurements: - temperature (average, maximum and minimum) - relative humidity (average, maximum and minimum) - wind speed average - radiation - altitude from sea level - latitude We manage to develop such script within dataTaker for this calculation, I have already included sensor information as well. You may replace the sensor with other brand as required. This is the script: ```` BEGIN&quot;EVAPTR&quot; PROFILE HOST_PORT BPS=4800 PROFILE HOST_PORT FUNCTION=SERIAL PROFILE SERSEN_PORT BPS=9600 PROFILE SERSEN_PORT DATA_BITS=8 PROFILE SERSEN_PORT PARITY=NONE PROFILE SERSEN_PORT FLOW=NONE PROFILE SERSEN_PORT MODE=RS422 PROFILE SERSEN_PORT FUNCTION=MODBUS_MASTER S1=0,4000,0,56 RS1M RA1M &#039;reading parameters &#039;Thies Clima US 4.9200.00.001: MODBUS RTU 1MODBUS(AD1,R3:5005,MBL,MES,&quot;T~degC&quot;,0.1,=101CV,W) 102CV(W)=101CV 1MODBUS(AD1,R3:5013,MBL,MES,&quot;RH~%&quot;,0.1,=103CV,W) 104CV(W)=103CV 1MODBUS(AD1,R3:5001,MBL,MES,&quot;WS~m/s&quot;,0.1,=105CV,W) 106CV(W)=105CV &#039;Kipp and Zonen CMP10: terminal 1+ and 1- 1V(S4,=107CV,W) 108CV(W)=107CV &#039;normal weather measurement every 15 minutes RB15M LOGONB 101CV(AV,&quot;T~degC&quot;)(MX,&quot;T Max~degC&quot;)(MN,&quot;T Min~degC&quot;) 103CV(AV,&quot;RH~%&quot;)(MX,&quot;RH Max~%&quot;)(MN,&quot;RH Min~%&quot;) 105CV(W)(AV,&quot;WS_AV~m/s&quot;) &#039;evapotranspiration calculation every day RC1D LOGONC 102CV(W)(AV,=1CV)(MX,=2CV)(MN,=3CV) 104CV(W)(AV,=4CV)(MX,=5CV)(MN,=6CV) 106CV(W)(AV,=7CV) 108CV(W)(AV,=8CV) &#039;Garmin 18x PC: HOST port 2SERIAL(&quot;\m[GPGGA,]\m[,]%2d[201CV]%f[202CV]\m[,]\m[,]\m[,]\m[,]\m[,]\m[,]\m[,]%f[9CV]\e&quot;) 9CV(&quot;Altitude~masl&quot;)=66 10CV(&quot;Latitude~deg&quot;)=201CV+(202CV/60) &#039;Date 20SV(&quot;Date&quot;,=51CV) 21SV(&quot;Month&quot;,=52CV) 22SV(&quot;Year&quot;,=53CV) &#039;calculation 11CV(&quot;Latitude~rad&quot;,FF2)=D2R(10CV) 12CV(&quot;Atmospheric Pressure~kPa&quot;,FF2)=101.3*((293-0.0065*9CV)/293)^5.26 13CV(&quot;Latent Heat~MJ/kg&quot;,FF2)=2.501-(2.361*3CV/1000) 14CV(&quot;Psychrometric Constant~kPa/degC&quot;,FF2)=(1.013/(1000*0.622))*12CV/13CV 15CV(&quot;Vapour Pressure T~kPa&quot;,FF2)=0.6108*E^(17.27*1CV/(1CV+237.3)) 16CV(&quot;Vapour Pressure T max~kPa&quot;,FF2)=0.6108*E^(17.27*2CV/(2CV+237.3)) 17CV(&quot;Vapour Pressure T min~kPa&quot;,FF2)=0.6108*E^(17.27*3CV/(3CV+237.3)) 18CV(&quot;Average Vapour Pressure~kPa&quot;,FF2)=(16CV+17CV)/2 19CV(&quot;Vapour Pressure Saturation Slope~ kPa/degC&quot;,FF2)=4098*15CV/(1CV+237.3)^2 20CV(&quot;Mod Psychrometric Constant~kPa/degC&quot;,FF2)=14CV*(1+0.34*7CV) 21CV(&quot;Actual Vapour Pressure~kPa&quot;,FF2)=(0.5*17CV*5CV/100)+(0.5*16CV*6CV/100) 22CV(&quot;Aerodinamic Term for PM~mm/day&quot;,FF2)=(20CV*900*7CV*(18CV-21CV))/((19CV+20CV)*(1CV+273.16)) 1IV(W)=(275*52CV/9) 2IV(W)=(9+52CV)/12) 3IV(W)=(53CV/4) 4IV(W)=(53CV+2-4*3IV)/3 23CV(&quot;No of Days in Julian calendar&quot;)=1IV-(2IV*(1-4IV))+51CV-30 24CV(&quot;Inv Relative Distance to the Sun~rad&quot;,FF2)=1+0.033*COS(2*PI*23CV/365) 25CV(&quot;Solar Declination~rad&quot;,FF2)=0.409*SIN(2*PI*23CV/365-1.39) 26CV(&quot;Solar Declination Angle~rad&quot;,FF2)=ACOS(-TAN(11CV)*TAN(25CV)) 27CV(&quot;Extraterrestrial Radiation~MJ/m2&quot;,FF2)=(118.08/PI)*24CV*(26CV*SIN(11CV)*SIN(25CV)+COS(11CV)*COS(25CV)*SIN(26CV)) 28CV(&quot;Solar Radiation~MJ/m2&quot;,FF2)=8CV*0.0864 29CV(&quot;Net Solar Radiation~MJ/m2&quot;,FF2)=(1-0.23)*28CV 30CV(&quot;Solar Radiation on clear sky~MJ/m2&quot;,FF2)=(0.75+2*10^-5*9CV)*27CV 31CV(&quot;Net Wave Radiation~MJ/m2&quot;,FF2)=4.903*(10^-9)*((2CV+273.16)^4+(3CV+273.16)^4)*(0.34-0.14*SQRT(21CV))*(1.35*(28CV/30CV)-0.35)/2 32CV(&quot;Net Radiation~MJ/m2&quot;,FF2)=29CV-31CV 33CV(&quot;Radiation Term~mm/day&quot;,FF2)=0.408*19CV*32CV/(19CV+20CV) 34CV(W)=33CV+22CV 34CV(&quot;Evapotranspiration~mm/day&quot;,FF2)=(34CV&lt;0)?0:34CV END ```` That script has 3 schedules: - schedule A that running every minute to read weather sensors. - schedule B that run every 15 minutes to calculate statistic from schedule A - schedule C that run every day to calculate evapotranspiration. Evapotranspiration itself will be calculated on daily basis using statistic of 1 minute measurement. Best regards, Rudy Gunawan
edited May 1 '20 at 1:59 pm
139
0
1
live preview
enter atleast 10 characters
WARNING: You mentioned %MENTIONS%, but they cannot see this message and will not be notified
Saving...
Saved
With selected deselect posts show selected posts
All posts under this topic will be deleted ?
Pending draft ... Click to resume editing
Discard draft