Hi Eric,
Could you explain about the condition of the logger when you deduced that the firmware is corrupted or lost?
What is the logger serial number and version of firmware?
Flashing all 4 lights indicates SW exception error which usually caused by the logger when trying to access ONINSERT.dxc file as part of upgrade files.
There are several reasons that cause this event and the most probable event is the logger does not have enough free memory to perform firmware upgrade.
If this is series 1 or 2 logger with an existing 7.06 firmware or older, then the issue is obviously not enough free memory.
Have you install DT driver on tour PC?
Is there any error message when the connection to your PC rejected?
This is one of the remedies for enabling connection to the logger if the driver is OK and no error message: triple push.
Push a button next to Ethernet port using paper clip three times, each press last for 2 seconds with 1 second interval in between.
This triple push will return the logger to factory default and halt the program. Hopefully it will solve your problem.
Best regards,
Rudy Gunawan
Hi Eric,
Could you explain about the condition of the logger when you deduced that the firmware is corrupted or lost?
What is the logger serial number and version of firmware?
Flashing all 4 lights indicates SW exception error which usually caused by the logger when trying to access ONINSERT.dxc file as part of upgrade files.
There are several reasons that cause this event and the most probable event is the logger does not have enough free memory to perform firmware upgrade.
If this is series 1 or 2 logger with an existing 7.06 firmware or older, then the issue is obviously not enough free memory.
Have you install DT driver on tour PC?
Is there any error message when the connection to your PC rejected?
This is one of the remedies for enabling connection to the logger if the driver is OK and no error message: triple push.
Push a button next to Ethernet port using paper clip three times, each press last for 2 seconds with 1 second interval in between.
This triple push will return the logger to factory default and halt the program. Hopefully it will solve your problem.
Best regards,
Rudy Gunawan