Support Forums
Trigger Schedule with more CV

Hello,

I have DT80 series3 software version 9.10.
I will start a schedule when 4 or 5 CV's changes from 0 to 1 or 1 to 0
Hoe can I configure this when I programming in dEX.
I can only configure 1CV (Advanced triggering)
In program language it must be RB1..9+CV ?

Thanks for help

Hello, I have DT80 series3 software version 9.10. I will start a schedule when 4 or 5 CV's changes from 0 to 1 or 1 to 0 Hoe can I configure this when I programming in dEX. I can only configure 1CV (Advanced triggering) In program language it must be RB1..9+CV ? Thanks for help

Hi Frank,

Unfortunately you can't target multiple CVs in dEX programming.
May I know the detail of the change of CVs to start schedule trigger?
I may have a solution for you.

Best regards,
Rudy Gunawan

Hi Frank, Unfortunately you can't target multiple CVs in dEX programming. May I know the detail of the change of CVs to start schedule trigger? I may have a solution for you. Best regards, Rudy Gunawan

Hello Rudy,

Thanks for Your reply.

In schedul A, I monitor 5AS every 500ms, every AS is a CV (1CV - 5CV)
When one of te 5AS changes from 0 to 1 or 1 to 0, I log the state of the 5AS in schedule B.

Grts Frank

Hello Rudy, Thanks for Your reply. In schedul A, I monitor 5AS every 500ms, every AS is a CV (1CV - 5CV) When one of te 5AS changes from 0 to 1 or 1 to 0, I log the state of the 5AS in schedule B. Grts Frank

Problem solved, I program the DT80 with DeTransfer and changed the Trigger command in 1..5CV.

Problem solved, I program the DT80 with DeTransfer and changed the Trigger command in 1..5CV.

Hi Frank,

Yes, DeTransfer is the only one which can overcome dEX limitation.

Because your requirement to detect 5 CV's state either rise or fall, calculation channel cannot cover it perfectly.
Thus you will need multiple channels to get the state which is not feasible in term of simplicity.

In DeTransfer you can solve this problem with a single line.

Best regards,
Rudy Gunawan

Hi Frank, Yes, DeTransfer is the only one which can overcome dEX limitation. Because your requirement to detect 5 CV's state either rise or fall, calculation channel cannot cover it perfectly. Thus you will need multiple channels to get the state which is not feasible in term of simplicity. In DeTransfer you can solve this problem with a single line. Best regards, Rudy Gunawan
26
4
2
live preview
enter atleast 10 characters
WARNING: You mentioned %MENTIONS%, but they cannot see this message and will not be notified
Saving...
Saved
With selected deselect posts show selected posts
All posts under this topic will be deleted ?
Pending draft ... Click to resume editing
Discard draft