Hi Roger,
It looks we solved it although we still have some small issues (the output *.csv shows all data twice, double columns).
<raw username="Kotao1, 1MODBUS"><![CDATA[1MODBUS(AD1,R4:34,MBF)("Tout, Kotao1")
1MODBUS(AD1,R4:36,MBF)("Tin, Kotao1")
1MODBUS(AD1,R4:2,MBF)("Protok, Kotao1")
1MODBUS(AD1,R4:4,=3CV,MBF)
4CV=3CV*277.77777777778/1000
]]></raw>
<raw username="Kotao2, 1MODBUS"><![CDATA[1MODBUS(AD2,R4:34,MBF)("Tout, Kotao2")
1MODBUS(AD2,R4:36,MBF)("Tin, Kotao2")
1MODBUS(AD2,R4:2,MBF)("Protok, Kotao2")
1MODBUS(AD2,R4:4,=1CV,MBF)
2CV=1CV*277.77777777778/1000]]></raw>
<raw username="Kotao3, 1MODBUS"><![CDATA[1MODBUS(AD3,R4:34,MBF)("Tout, Kotao3")
1MODBUS(AD3,R4:36,MBF)("Tin, Kotao3")
1MODBUS(AD3,R4:2,MBF)("Protok, Kotao3")
1MODBUS(AD3,R4:4,=5CV,MBF)
6CV=5CV*277.77777777778/1000]]></raw>
<raw username="Kotao4, 1MODBUS"><![CDATA[1MODBUS(AD4,R4:34,MBF)("Tout, Kotao4")
1MODBUS(AD4,R4:36,MBF)("Tin, Kotao4")
1MODBUS(AD4,R4:2,MBF)("Protok, Kotao4")
1MODBUS(AD4,R4:4,=7CV,MBF)
8CV=7CV*277.77777777778/1000]]></raw>
</schedule>
</schedules>
</config>
Once we found how it works it is very easy and straightforward. We are still working with a DT80 but next week we replace with a DT85 to have more possibilities with analog signals, counters etc. It is a city heating plant with 4*58MW on crude oil. Interesting...
Best regards,
Peer
Hi Roger,
It looks we solved it although we still have some small issues (the output *.csv shows all data twice, double columns).
<raw username="Kotao1, 1MODBUS"><![CDATA[1MODBUS(AD1,R4:34,MBF)("Tout, Kotao1")
1MODBUS(AD1,R4:36,MBF)("Tin, Kotao1")
1MODBUS(AD1,R4:2,MBF)("Protok, Kotao1")
1MODBUS(AD1,R4:4,=3CV,MBF)
4CV=3CV*277.77777777778/1000
]]></raw>
<raw username="Kotao2, 1MODBUS"><![CDATA[1MODBUS(AD2,R4:34,MBF)("Tout, Kotao2")
1MODBUS(AD2,R4:36,MBF)("Tin, Kotao2")
1MODBUS(AD2,R4:2,MBF)("Protok, Kotao2")
1MODBUS(AD2,R4:4,=1CV,MBF)
2CV=1CV*277.77777777778/1000]]></raw>
<raw username="Kotao3, 1MODBUS"><![CDATA[1MODBUS(AD3,R4:34,MBF)("Tout, Kotao3")
1MODBUS(AD3,R4:36,MBF)("Tin, Kotao3")
1MODBUS(AD3,R4:2,MBF)("Protok, Kotao3")
1MODBUS(AD3,R4:4,=5CV,MBF)
6CV=5CV*277.77777777778/1000]]></raw>
<raw username="Kotao4, 1MODBUS"><![CDATA[1MODBUS(AD4,R4:34,MBF)("Tout, Kotao4")
1MODBUS(AD4,R4:36,MBF)("Tin, Kotao4")
1MODBUS(AD4,R4:2,MBF)("Protok, Kotao4")
1MODBUS(AD4,R4:4,=7CV,MBF)
8CV=7CV*277.77777777778/1000]]></raw>
</schedule>
</schedules>
</config>
Once we found how it works it is very easy and straightforward. We are still working with a DT80 but next week we replace with a DT85 to have more possibilities with analog signals, counters etc. It is a city heating plant with 4*58MW on crude oil. Interesting...
Best regards,
Peer