Relay click each time DT80 wakes

Just wondering if the relay flicking each time the logger wakes can be prevented?
I think in time at 1 second sampling this will kill the relay in time?
Thanks in advance for any suggestions

Just wondering if the relay flicking each time the logger wakes can be prevented? I think in time at 1 second sampling this will kill the relay in time? Thanks in advance for any suggestions

Good afternoon MLCarter,

The relays clicking means the logger is taking a sample and is part of the normal operation.
The relays have been carefully selected for the task and are very unlikely to fail

Have a read of http://www.thermofisher.com.au/show.aspx?page=/ContentAUS/Manufacturing-Processing/Industrial-Loggers/DataTaker/DataTaker-FAQ/DT80-FAQ/DT80-Mechanical.html. The MTBF is 1,000,000 hours.

Cheers

Roger

Good afternoon MLCarter, The relays clicking means the logger is taking a sample and is part of the normal operation. The relays have been carefully selected for the task and are very unlikely to fail Have a read of http://www.thermofisher.com.au/show.aspx?page=/ContentAUS/Manufacturing-Processing/Industrial-Loggers/DataTaker/DataTaker-FAQ/DT80-FAQ/DT80-Mechanical.html. The MTBF is 1,000,000 hours. Cheers Roger