Modbus Input

I am sorry if the question appears too newbie... With MODBUS/ RS485 compliance, does it mean that I can configure the following...

Scenario:
SENSORS 3 x load cell with MODBUS re-transmitter 4 x displacement transducer, direct connection 1 x measurement system with serial output, re-transmitted via MODBUS.

Basically, these are my current problems: Load cells are connected to a digital display unit that re-transmit in 4-20mA signal, read by a DT50. Because of the multiple translation, the displayed load is not same as what is logged on the DT50.

A digital output from the display unit read by the DT80 should fix the problem. I have a measurement device that outputs in serial mode, but the DT50 cannot read that. MODBUS should fix that too. I suppose I should wire the 2 re-transmitter in series under RS485 protocol and then connect that to the DT80.

Howzat?

Regards,
CW Wong

I am sorry if the question appears too newbie... With MODBUS/ RS485 compliance, does it mean that I can configure the following... Scenario: SENSORS 3 x load cell with MODBUS re-transmitter 4 x displacement transducer, direct connection 1 x measurement system with serial output, re-transmitted via MODBUS. Basically, these are my current problems: Load cells are connected to a digital display unit that re-transmit in 4-20mA signal, read by a DT50. Because of the multiple translation, the displayed load is not same as what is logged on the DT50. A digital output from the display unit read by the DT80 should fix the problem. I have a measurement device that outputs in serial mode, but the DT50 cannot read that. MODBUS should fix that too. I suppose I should wire the 2 re-transmitter in series under RS485 protocol and then connect that to the DT80. Howzat? Regards, CW Wong

Good afternoon CW,

At the moment the DT80 series 1 is only a slave device. That is it can be configured to be read by a SCADA system as a MODBUS device.

We do not yet have the capability to set the DT80 as the master to request data from MODBUS devices.

Cheers,
Roger

Good afternoon CW, At the moment the DT80 series 1 is only a slave device. That is it can be configured to be read by a SCADA system as a MODBUS device. We do not yet have the capability to set the DT80 as the master to request data from MODBUS devices. Cheers, Roger