Hello Rudy, Is there any way to assign a manual channels whole consumption (mA) in any interval (hour/day/etc...).

Best Regards
Gonzalo

Hello Rudy, Is there any way to assign a manual channels whole consumption (mA) in any interval (hour/day/etc...). Best Regards Gonzalo

Hi Gonzalo,

If you plan to measure cumulative consumption, you can put consumption channel at the shortest interval, then add an increment CV. If you call that CV at higher interval you can get the cumulative reading. Re zero that CV if required.
Example (this is for precipitation but the same method applies to consumption):

RA1M
1HSC(=1CV,W)
2CV(W)=2CV+1CV

RB1H
2CV("Rain~mm/h")
3CV(W)=3CV+2CV
2CV(W)=0

RC1D
3CV("DailyRain~mm")
3CV(W)=0

Best regards,
Rudy Gunawan

Hi Gonzalo, If you plan to measure cumulative consumption, you can put consumption channel at the shortest interval, then add an increment CV. If you call that CV at higher interval you can get the cumulative reading. Re zero that CV if required. Example (this is for precipitation but the same method applies to consumption): ```` RA1M 1HSC(=1CV,W) 2CV(W)=2CV+1CV RB1H 2CV("Rain~mm/h") 3CV(W)=3CV+2CV 2CV(W)=0 RC1D 3CV("DailyRain~mm") 3CV(W)=0 ```` Best regards, Rudy Gunawan