Hi Rheniumjoe,
It is correct dataTaker can convert mV from thermocouple to temperature and the process happens internally (no need to add calculation for conversion).
When you have mA signal that need conversion to temperature, you can utilise scaling function. Usually the controller will provide an information about 4-20 mA representation over temperature range (in your case thermocouple reading). You can use that information for scaling.
For example:
Thermocouple type C has a range of 0- 2320 degC, but the controller use 4-20 mA to represent 0-1500 degC, then the scaling would be (remember 4-20 mA channel in DT will give a result of 0 - 100% in place of 4-20mA):
BEGIN"READ"
S1=0,1500,0,100
RA1M LOGONA
1*L(S1,"Temperature~degC")
END
Best regards,
Rudy Gunawan