DEX 2.1.11

When i use the run wizard to set my mains frequency to 60HZ and temperature units to Fahrenheit , I continue to the end where i click on submit. When i collect my data it is in Celsius and when i check logger regional settings i see 50HZ and Celsius. I am using a DT85 with v9.22 firmware.

When i use the run wizard to set my mains frequency to 60HZ and temperature units to Fahrenheit , I continue to the end where i click on submit. When i collect my data it is in Celsius and when i check logger regional settings i see 50HZ and Celsius. I am using a DT85 with v9.22 firmware.
edited Sep 16 '20 at 9:40 pm

Hi mwisniewski,

After you send all the setting using the Wizard, please recheck the parameters again via Command Interface. Please use P11 for frequency and P36 for temperature units, they should return 60 and 1 for Fahrenheit.

If not please send me the screenshot of the setting process.

Best regards,
Rudy Gunawan

Hi mwisniewski, After you send all the setting using the Wizard, please recheck the parameters again via Command Interface. Please use P11 for frequency and P36 for temperature units, they should return 60 and 1 for Fahrenheit. If not please send me the screenshot of the setting process. Best regards, Rudy Gunawan