MODBUS communication in DT is available on both serial port and Ethernet port. If using serial port the popular name is MODBUS RTU while using Ethernet has a name of MODBUS TCP.
On using MODBUS TCP there is no specific Master Slave arrangement, the one which send a request would be Master and the one which receive a request would be Slave. So you can have dataTaker to read sensor through MODBUS TCP (as a Master) and being read by PLC using the same MODBUS TCP (as a Slave).
But you must pay attention on the timing and the interval of reading (sensor reading or PLC reading). It is recommended not to use a fast reading interval (i.e.: below 1 second) due to sequential process in the logger and non-synch timing with the PLC.
Best regards,
Rudy Gunawan