General Discussions
dt85 ftp

Hi,

I've been using a DT85 series 4 for logging several 4:20mA signals, and I'm configuring the DT-85 using DEX-2.
the DT85 had displayed all the signal correctly on its display, however when I tried sending a CSV file using FTP, nothing was sent to the FTP server.

her is the DXC

BEGIN"config"
'Generated by new dEX-2
password=""

S1=0,500,4,20""
S2=0,5000,4,20""
S3=0,25,4,20""
S4=0,1000,4,20""
S5=0,100,4,20""
S6=0,100,4,20""
S7=-5,3,4,20""

RS1S

RA"Schedule_1"("b:",ALARMS:OV:100KB:W60,DATA:OV:1MB)1M
LOGONA
2#I(N,"CO~mg/Nm3",=1001CV,LM,S1,NA,100)
3#I(N,"SO2~mg/Nm3",=1004CV,LM,S2,NA,100)
4#I(N,"O2~%Vol",=1007CV,LM,S3,NA,100)
5#I(N,"NOx~mg/Nm3",=1010CV,LM,S4,NA,100)
6#I(N,"Opacity~%",=1013CV,LM,S5,NA,100)
CALC("Pressure~KPa",=1027CV,LM)=(1027CV+1000)/10
8TK("Temperature~degC",=1023CV,LM,NA)
1DS("UPS~",=1026CV,LM)
DO{copyd dest="ftp://admin:c2014@10.255.229.77:21//141SuizElec?priority=NORMAL&interface=ETHERNET" format=CSV sched=A data=Y alarms=N start=new }
7#I(N,"Pressure~mBAr",=1019CV,LM,S7,NA,100)

END

Kind regards,
Beshoy

Hi, I've been using a DT85 series 4 for logging several 4:20mA signals, and I'm configuring the DT-85 using DEX-2. the DT85 had displayed all the signal correctly on its display, however when I tried sending a CSV file using FTP, nothing was sent to the FTP server. her is the DXC BEGIN"config" 'Generated by new dEX-2 password="" S1=0,500,4,20"" S2=0,5000,4,20"" S3=0,25,4,20"" S4=0,1000,4,20"" S5=0,100,4,20"" S6=0,100,4,20"" S7=-5,3,4,20"" RS1S RA"Schedule_1"("b:",ALARMS:OV:100KB:W60,DATA:OV:1MB)1M LOGONA 2#I(N,"CO~mg/Nm3",=1001CV,LM,S1,NA,100) 3#I(N,"SO2~mg/Nm3",=1004CV,LM,S2,NA,100) 4#I(N,"O2~%Vol",=1007CV,LM,S3,NA,100) 5#I(N,"NOx~mg/Nm3",=1010CV,LM,S4,NA,100) 6#I(N,"Opacity~%",=1013CV,LM,S5,NA,100) CALC("Pressure~KPa",=1027CV,LM)=(1027CV+1000)/10 8TK("Temperature~degC",=1023CV,LM,NA) 1DS("UPS~",=1026CV,LM) DO{copyd dest="ftp://admin:c2014@10.255.229.77:21//141SuizElec?priority=NORMAL&interface=ETHERNET" format=CSV sched=A data=Y alarms=N start=new } 7#I(N,"Pressure~mBAr",=1019CV,LM,S7,NA,100) END Kind regards, Beshoy
edited Dec 17 '20 at 8:06 am

Hi Beshoy,

Apology for late respond.

Can you please enable FTP transfer diagnostic and try to send a data? However before you perform the diagnostic, please clear all of the failed session. You can clear all session by sending SESSION CLEAR from command window.

My best guess would be the FTP server security setting on writing or renaming action (if the network setting is correct and no mistake on username/ password of the FTP server).

Best regards,
Rudy Gunawan

Hi Beshoy, Apology for late respond. Can you please enable FTP transfer diagnostic and try to send a data? However before you perform the diagnostic, please clear all of the failed session. You can clear all session by sending SESSION CLEAR from command window. My best guess would be the FTP server security setting on writing or renaming action (if the network setting is correct and no mistake on username/ password of the FTP server). Best regards, Rudy Gunawan
151
1
2
live preview
enter atleast 10 characters
WARNING: You mentioned %MENTIONS%, but they cannot see this message and will not be notified
Saving...
Saved
With selected deselect posts show selected posts
All posts under this topic will be deleted ?
Pending draft ... Click to resume editing
Discard draft