Hello there,
I need a simple wiring scheme for flowmeter MES 20 to Datataker DT85GM
It should have 3 wires (Pulse, 5-25V positive, and shield).

606d39ad0c01d

Do I need external 24V power source and, if needed, how do I connect it?

Many thanks.
Peter

Hello there, I need a simple wiring scheme for flowmeter MES 20 to Datataker DT85GM It should have 3 wires (Pulse, 5-25V positive, and shield). ![606d39ad0c01d](serve/attachment&path=606d39ad0c01d) Do I need external 24V power source and, if needed, how do I connect it? Many thanks. Peter
edited Apr 7 '21 at 5:51 am

Hi Thuc,

The sensor will need to use the 5-25V pin and shield pin (sensor) to power it up; you can use 24V or any power sources within that range.

Then you have to connect the pulse pin (sensor) to 1D (logger) and shield pin (sensor) to DGND (logger), use a low-speed counter.

Or, instead of 1D, you can use a 1C pin (logger) and use a high-speed counter.

Best regards,
Rudy Gunawan

Hi Thuc, The sensor will need to use the 5-25V pin and shield pin (sensor) to power it up; you can use 24V or any power sources within that range. Then you have to connect the pulse pin (sensor) to 1D (logger) and shield pin (sensor) to DGND (logger), use a low-speed counter. Or, instead of 1D, you can use a 1C pin (logger) and use a high-speed counter. Best regards, Rudy Gunawan
86
1
2
live preview
enter atleast 10 characters
WARNING: You mentioned %MENTIONS%, but they cannot see this message and will not be notified
Saving...
Saved
With selected deselect posts show selected posts
All posts under this topic will be deleted ?
Pending draft ... Click to resume editing
Discard draft