Hi Charles,
Since the sensor has 4-20 mA output and uses a junction box, I assume you try to utilize the internal shunt resistor. It would be neat on wiring, but because the internal shunt resistor is separated by relay, the logger would only close the relay when the measurement is due.
Obviously, because the shunt resistor is not connected to the 4-20 mA circuit, you may experience a required delay on measurement (long wait time). I recommend you to use an external 100 ohms shunt resistor instead and perhaps resistor network type to get the wiring neat for each terminal. Furthermore, if you utilize the external shunt resistor, you can connect more than one sensor per terminal.
Best regards,
dataTaker Expert
Hi Charles,
Since the sensor has 4-20 mA output and uses a junction box, I assume you try to utilize the internal shunt resistor. It would be neat on wiring, but because the internal shunt resistor is separated by relay, the logger would only close the relay when the measurement is due.
Obviously, because the shunt resistor is not connected to the 4-20 mA circuit, you may experience a required delay on measurement (long wait time). I recommend you to use an external 100 ohms shunt resistor instead and perhaps resistor network type to get the wiring neat for each terminal. Furthermore, if you utilize the external shunt resistor, you can connect more than one sensor per terminal.