Keaton posted Apr 19 '19 at 3:58 am
I need to measure an analog voltage of +/- 5 Vdc. I know I need to set the channel 10:1 attenuator in order to do this. When I configure the input range to '30V Input' on my channel in dEX and save to the logger, I get the error message as seen in the attachment.

I've tried doing the command through the command window in dEX also [9HV(GL30V)]. Then it seems to be accepted, but when I apply a
5cb93ae46528d
recent by Keaton  ·  Apr 19 '19 at 4:05 am
14
1
eric posted Apr 18 '19 at 4:54 pm
Hi Support,

I am trying to send the follow data to the RS485 port in HEX: 68 04 00 04 08 by sending \104\04\00\04\08
however it appears that only 68 04 04 08 is sent, the 0x00 in the middle was not sent.

Is there a workaround for this?

Thanks very much for the help

BR
Eric

recent by admin  ·  Apr 18 '19 at 4:57 pm
55
3
Hillzider posted Apr 18 '19 at 4:46 pm
Hi,

I am using the +5V output to power a humidity sensor, I have used the command +5VSW=1 and set the logger up so that the 12V subsystem is continuously powered. However when I run the logger, the +5V works for short scan times (5secs) but for 15min scans the +5V does not switch on and so the sensor gives a bad reading.

Does whether having the USB connected affect whether the +5V SW is
recent by Lokesh  ·  Apr 18 '19 at 4:52 pm
32
1
ITS posted Apr 18 '19 at 4:48 pm
Hi

I am looking to read PT100 sensors and digital inputs from a novus digiral module http://www.novus.com.br/site/default.asp?TroncoID=621808&SecaoID=819191&SubsecaoID=0&Template=../catalogos/layout_produto.asp&ProdutoID=748482

Can you confirm how this can be done with the dt85 sensor port I was looking at something like 1MODBUS(AD2,R1:1,=12CV) to read the digital state a
recent by admin  ·  Apr 18 '19 at 4:49 pm
31
4
chintanp posted Apr 18 '19 at 4:37 pm
We want to use datalogger to measure two channels - load cell and strain gage simultaneously, with a schedule such that, the data is recorded on a switch press and not at a fixed time interval.

I was reading the manual and I found that schedules can be triggered on external events, (Pg - 43 of DT-80 Users manual).

I feel a trigger on switch press should be "Trigger on rising transition
recent by chintanp  ·  Apr 18 '19 at 4:44 pm
47
9
senthilkumaranms posted Apr 18 '19 at 4:18 am
Huge Fluctuations in measurement. I have connected strain Gage and full bridge load cell for measurement.

noticing very high fluctuation in the measurement. If I touch the DAQ body, strain values and all other sensor values whatever connected in DAQ is varying heavily. I have done the ground connection also. still variations in strain measurements is very high.

It is not because of tempe
recent by takima958  ·  Apr 18 '19 at 4:32 pm
69
12
mtseitzler posted Apr 18 '19 at 4:16 am
After downgrading our firmware to 9.10.4890 per Datataker tech support recommendation our DT85 (series 3) is going through resets about every four days causing the loss of data during the reset.

In the event log the reset error is "Reset 9.10.4890 PLL/WDOG/DEBUG (c860400d)".

Currently we have two schedules running; one 15 sec and one 1 min. In the 15 sec. we read 12 analog and 4 modbus c
recent by admin  ·  Apr 18 '19 at 4:09 pm
20
1
austriacus posted Apr 18 '19 at 4:44 am
We have a similar issue with the logger stopping to respond to be read through Modbus TCP/IP.
The logger works fine for 24-48 hours and then stops communicating over the Modbus TCPIP.
The setup we are using a DT85 connected to 16 CEM channels – a total of 400 HV I/O (we are reading 4-20mA pressures transmitters over a 250Ohm resistor).
The DT85 is connected via a freewave radio and
recent by admin  ·  Apr 18 '19 at 4:05 pm
31
1
Dear all,

I have been experimenting using a DT85 Series 2 to measure relative humidity using the Wet/Dry bulb method. I have been taking the measurements using a pair of K type thermocouples - one of which is 'wet.'

I have tried using the routine outline in the FAQ through DeTransfer. The problem is that the calculation in the formula is quite different from that using a psychrometric cha
recent by admin  ·  Apr 18 '19 at 3:41 pm
27
1
rheem posted Apr 18 '19 at 4:49 am
I have contacted technical support in relation to this issue, but this is a more general question regarding current loops.

When you configure a channel for a current loop (as opposed to a current input), without any scaling, the logger should be 'reading' a 0-100% figure. This is related to the 4-20mA range of these current loop sensors. Is that correct?

If I have configured channels for
recent by Roger  ·  Apr 18 '19 at 4:52 am
24
3
rheem posted Apr 18 '19 at 4:48 am
Hello,

I have searched high and low in the manual and FAQ without luck. The DT85 Series 2 has TWO power supply inputs for the switched excitation and shunt resistor. They are labeled exactly the same (EXT * and EXT #).

My question: Are these inputs tied together (is one EXT * electrically equivalent to the other)? Is one power input used for certain analog channels? If I am using switch
recent by Roger  ·  Apr 18 '19 at 4:52 am
38
6
Hi all, hope that somebody can help me with this

I'm using analog sensors connected to a Voltage amplifier with a three conductor cable, one to signal out, one to ground and the third for power supply. The amplifier has an terminal to connect the power supply input +DC voltage (Vcc 5-24 VDC), but is not clear for me to which terminal in the datataker would correspond the power supply connecti
recent by Cmin  ·  Apr 18 '19 at 4:35 am
17
3
malsabti posted Apr 18 '19 at 1:00 am
I hope everyone is doing well.

I have the DT85 series 3 dataTaker and I would like to hook up string pots to it for our testing lab. I have no experience with the data taker and would love any help anyone can provide

I've emailed tech support and they suggested that it might by a voltage divider pot but I'm sure that it reads resistance. I even placed a multi-meter across the green and
5cb7be098c805
recent by admin  ·  Apr 18 '19 at 1:08 am
69
2
cbasler posted Apr 18 '19 at 12:52 am
Hello,

I want to run the DT85 via USB, so therefore I need a USB-Driver. Unfortunately, the Driver on the page seems to be missing. Also, the dEX software platform, which I thought I could find is leading me to an "not found" page. Could you help me with that problems?

Greetings,
Clemens Basler

recent by cbasler  ·  Apr 18 '19 at 1:06 am
47
1
ITS posted Apr 17 '19 at 11:59 pm
Hi
I have a dt85 whereby it is continually crashing and stops logging cannot be connected to, & front panel becomes non responsive.
the only way to get the logger back on line is to preform a reset and once this is done the logger reverts back to a much older date.
I have checked various possible causes but to no avail, I also have a UPS backup system on the logger but the problem p
recent by admin  ·  Apr 18 '19 at 12:49 am
538
3
Greg posted Apr 18 '19 at 12:00 am
I've am attempting to connect to a new DT85 Series 4, but I'm having trouble connecting to it via USB and via Ethernet. My laptop has Windows 10 OS.

I have DeLogger, DTUSB and DeTransfer all installed. I have set Internet Explorer 11 as my default browser as that seems to be the preferred browser.

When I plug in via USB the dtUSB app starts in the background. When I open it up it looks li
recent by admin  ·  Apr 18 '19 at 12:35 am
21
2
Andyc160 posted Apr 18 '19 at 12:02 am
I have a DT85 series 4 running v9.20

Whilst the logger is logging i want to unload a time frame of data. i try to connect via Ethernet and the address displayed on the LCD screen. the browser tries to go through its usual process but doesn't display the usual configure, monitor page?

i had to perform a hard reset which as a result looses all data stored.

i have the logger set for 5 s
recent by admin  ·  Apr 18 '19 at 12:33 am
23
2
jodieugent posted Apr 18 '19 at 12:03 am
For are thesis we are doing research to the hygrothermal behavior of wooden walls. To make measurements we are using the datataker dt85.

Our problem is now that the logger only gives the results for approximately 10 days, what's about 10 000 data, while in the manual of the datalogger is written that it has a memory for about 10 million data. Can we change anything to the setting so we can c
recent by admin  ·  Apr 18 '19 at 12:29 am
16
1
I have taken over a DT85 programmed by someone else. I have connected to the DT85. I need to change some IP addresses as a new router has been installed.



I can't open the command box to change IP addresses.
I am steep on the learning curve here!
I get the message on the attachment.
I have opened port 843, still no joy.

Any ideas?


5cb7b1a9c4537
recent by admin  ·  Apr 18 '19 at 12:23 am
29
1
RPE_GER posted Apr 18 '19 at 12:09 am
Hello together,

I try to set the Date with the reading GPS Date but it doesn't work.

$GPRMC,094924.000,A,4856.8229,N,00824.6182,E,0.47,331.35,150118,,,A69
2SERIAL("\e\m[$GPRMC],%f,%1s,%f,%1s,%f,%1s,%f,%*f,%2d[420CV]%2d[421CV]%2d[422CV]",W)

420CV("Day") 'Show Day
421CV("Month") 'Show Month
422CV(W)=422CV+2000
422CV("Year") 'Show Year

Alarm(414CV==1)"Date update
recent by admin  ·  Apr 18 '19 at 12:22 am
24
1
Thaar posted Apr 18 '19 at 12:11 am
Welcome

We have DT85G recently, and we need to connect to it 3-wires LVDT of monitran company. we did several attempts of connection and all these gave an error reading.

The LVDT features are stroke 125 mm , supply voltage =9 to 24 Volts Dc(regulated) and its connection details are RED for supply volts DC , Blue for 0 volts DC and green for output(0-5).

With my regards

recent by Roger  ·  Apr 18 '19 at 12:12 am
29
5
Dear all,

I need to connect several Multi function Energy meter to DT85 using RS485.
I have never worked before with modbus /serial communication.

I checked manual and says need to set profile etc. But silly question, where do i put this code ? as i have always used deX for making program so it was pretty straight forward.

Should i use Detransfer to put command or can it be done
recent by admin  ·  Apr 17 '19 at 12:57 pm
29
5
Friedrich posted Apr 17 '19 at 12:43 pm
Hi,

I am using modbus tcp/ip for reading a multiple phase meter. Because I have to specify the IP-address of the meter the datataker is logging in each time I read the meter. Is there a way to avoid logging in each time when the datataker reads the meter?

Best Regards,
Friedrich Völlink

recent by admin  ·  Apr 17 '19 at 12:57 pm
28
3
We've got a Dataker DT85 logger which scans data every 15s and logs the average of 4 readings every minute. The data is captured via DigiRails.

For quite sometime now, the logger keeps on crashing after a a few hours of operation. We've tried various settings and even had a replacement logger but even the replacement logger crashes after a while. Both the original and replacement loggers are
recent by admin  ·  Apr 17 '19 at 12:52 pm
13
1
We are using a DT85 to measure the voltage drop over a high resistance (> 1Mohm) with the aid of an external voltage supply. When we limit the supply to a 3V input and thus the measurements to the 3V range on the data logger the measurements are correct as confirmed by use of a multimeter. We would like to measure at higher voltages to get more accurate readings. When using the attenuator howe