Hello,

Was inserting new code on a recently acqqired DT80 series 4 on Dex 2 and applied some changes to the logger program, as I've done before, but now it is not able to obtain an IP address.

Dex-2 tries to heartbeat the logger but never manages to connect. I've accessed the logger through its IP on the browser and can see the event log:

"Ethernet Interface: cannot obtain an IP Addre
133
4
Hello DataTaker Support Team,

i have a simple question. I like to replace my old DT80 series2/3 with the new DT80M serie 4. The problem is, when i replaced a series2 with a series3 DT i just had to copy and paste the config. Sadly, this method isn´t working for the current version. I already searched the forum because i heard, that there exists already a work around for this problem, b
recent by MarkH  ·  Aug 23 '21 at 10:08 am
74
1
C.Jackson posted Aug 15 '21 at 4:21 am
I have a wireless load cell from Straightpoint and the output is RS485. I would like to bring this into a DT80 series 2 but am having trouble. I assume this would be done as a Modbus input? I also need to know what syntax I need to use to poll the device to get the data out of it?
If anyone has any experiance with setting this connection up it would be greatly appreciated.

55
2
Wolfy27 posted Jul 8 '21 at 11:50 am
I have connected a CEM20 to a DT80W, using USB to download data the headers are completely wrong for the channels.
I have 101*TT("Temp 1") through to
105-TT("Temp14")

I have the CEM plugged into channel 1 on the DT.

The downloaded data in csv file gives me
Therm 1, Therm 1, Therm 1.........and so on. Including the VEXT channel

When unload through delogger5 headers are correc
recent by Wolfy27  ·  Aug 6 '21 at 11:31 pm
65
1
Hi

I have suddenly encountered problems with the readings from our DT85G. The temperatures readings we get is 327.7 degC, or OverRange.
When I run a test I get the following report below.
The Shunt(100R) gives a value of 0.0 Ohm.
I now wonder if and how this can be repaired and if a lightning strike could have cause this error?

Best regards
Josef

TEST report generated at
104
5
MarkH posted Jul 6 '21 at 12:25 pm
Hello Support Team,

i hope my question is very simple. The problem is, that i have to buy new USB-Sticks for 8 DT Serie2/3. As u know, some USB-sticks are working and some not. So i wanted to ask if u know a brand or if u have a link to a seller where i can buy sticks which are def working (im from germany). Or u have a work around for the sticks i already bought but i tried nearly everything
206
2
Ladislav posted Jun 4 '21 at 10:54 am
Hello,

I'm using series3 DT80. After firmware upgrade to last version v9.22, logger
was working fine for a week, untill I wanted to clear logger internal memory using command DELALLJOBS. Result of "delalljobs" command was that current job was terminated but message SW exception appeared. Moreover, internal disk was not cleared.

Now, logger display show message "No current job", but I
recent by Ladislav  ·  Jun 24 '21 at 1:48 pm
490
9
Our current dEX web interface is not compatible to flash player plugin version 30 or newer, thus you will experience slow response on key stroke to the display. We will release the next version of dEX free of flash player, however for a time being you will need to downgrade flash player plugin from your web browser.

Some plugin is bundled with web browser such as Google Chrome, you will need
5dd5c7c8088db
84
1
hello, i need help installing flash player v.29. I managed to delete the Macromed folder in System32 and in the registry editor (regedit). From then on, windows allowed to install previous version, but at the end of the installation bar 100% message appears "it was not possible to register ActiveX control for flash player"... I prefer to use Dex original version because I am more familiar with th
36
1
hello, I'm a layman on datataker, but here in Brazil I've already performed some data collection activities with SGVW in wind tower base foundations with great use. We have now bought another DT80G series4. I need help profiling a concrete sample behavior research test, to create a schedule to read 8 SGVW, namely:

every 30 seconds for 3 hours, then...
every 5 minutes for 3 days, then...
every
49
1
Actinide posted May 25 '21 at 11:12 am
Hello fellow data taker users.

This is my first post, so hopefully I can find some answers to my question.

I have multiple datataker DT85's + CEMs being used for a laboratory.

Since upgrading to the DEX v2.0 software I am currently having numerous issues, the main one being able to quickly view which DT is recording. I currently have to check by using the command function to see if th
49
1
Hi all,

we are facing an issue with our datataker DT80 in downloading some saved data of a schedule configured with the previous version of the software. When I enter the explore data window, the software recognises the quantities with the channels but at the momento of downloading all the data, the software stucks. I don't know if it is a problem of not compatible versions or just a matter
52
0
Ixus posted May 27 '21 at 7:40 am
Hello,

I'm trying to find out that are the ports in the dtusb hard coded?

I made the datataker more secure by changing the defaults ports (the http 80 ports get too much unwanted traffic) but when connected with usb, I can't get the DEX2 working anymore. I'm afraid that this is caused by dtusb, because it reports the default ports only. I tried to look this from manual. So am I right tha
82
1
SJRJ posted Apr 1 '21 at 12:25 pm
We are using a datataker (Model: DT85 GM Series 4)in our lab to take strain gauges reading. We have another datataker (Model: DT85 GM Series 3) also in our lab in use. When we connected the same strain gauge to both datatakers separately, both showed different readings. The DT85 Series 4 showed it in the ‘6000-7000’ range and the DT85 Series 3 showed it in the ‘10000-11000&rsquo
6065ad7d73b81
145
3
Juergen posted Mar 26 '21 at 8:10 am
To collect data from a serial device we use manual channels.
There are some problems to realize it with dEX-2:

The available space to enter commands is limited. (We could solve it by splitting it to several channels)
After saving the configuration to a file and reloading it, there are suddenly many blank lines inserted that we did not originally enter. After each save, this seems to double
1.6k
4
dataTaker Expert posted Jan 15 '21 at 6:06 am
Hi,

This post will explain how to migrate your existing dEX program written with the flash player version of dEX to dEX 2.0.

If the program (written in the old dEX) already in the logger, dEX 2.0 can convert it straight away if there is no manual channels (i.e.: MODBUS channels) and/ or alarms declaration.

However if you have manual channels and/ or alarm declaration, you will find "d
6001285f7aa8f
88
1
jaisantosh.d posted Mar 26 '21 at 10:44 am
Hi Facing an Issue with DT82i connectivity.
I was able to connect device and create channels and even sent data using Modbus TCP, but all of sudden the status it is showing is "device is currently offline" in dEX 2.1.18 application and even web interface is not working its just loading.
As in Device LCD screen it was showing message "SW Exception" but after deleting all jobs from the device
330
3
Alicia posted Mar 5 '21 at 2:36 am
Hi,

When using dEX-2 to apply a schedule to our dataloggers, the dataloggers now give the error "SW Exception".

Some times the schedule does no load and there is "no config", sometimes it does load. But we get the error code every time we try to apply the schedule. The dataloggers and dEX 2 were working fine for two weeks but then this issue started. At first it was every second time but
99
1
jaisantosh.d posted Mar 25 '21 at 9:37 am
Hi Team,
I have purchased a DataTaker DT82i to communicate with the flow meter and Temp sensor and to send that data to our IOT gateway.
I was able to configure Internal Tags and see that data in web interface using DEX 2.1.18 for Channel creation.
Able to read those Internal tags as well using Modbus TCP/IP, in PC but when I connected Datalogger to IOT gateway the Modbus status was ok b
56
1
Juergen posted Mar 22 '21 at 7:52 pm
Hi,
we run the DT80 behind a NAT router and want to access it via FTP. As our FTP client uses passive FTP, the router has IP forwarding for port 21 and port range 1024-5000.
Unfortunately it doesn't work. To see what happens I have set P56=8
Here I could see, that after login the command for passive mode is received, that will be answered by the logger with its internal IP address and a
202
6
neceel posted Dec 10 '19 at 10:57 am
What is it?

EVENT ,2019/12/10,10:28:39,0.813232,"Damaged accounts DB"
EVENT ,2019/12/10,10:28:39,0.901733,"Damaged accounts DB"
EVENT ,2019/12/10,10:28:49,0.803344,"Damaged accounts DB"
EVENT ,2019/12/10,10:28:49,0.905883,"Damaged accounts DB"
EVENT ,2019/12/10,10:28:59,0.780517,"Damaged accounts DB"
EVENT ,2019/12/10,10:29:00,0.089355,"Damaged accounts DB"
EVENT
recent by ashwin.m  ·  Mar 26 '21 at 2:58 pm
57
1
C.Jackson posted Mar 9 '21 at 5:48 am
I am wanting to connect a CanGate to a DT80 series 2 and the literature I have read still points me to using DeLogger instead of Dex2. Does anyone know if you can still use the CanGate and Dex2? Its for a stationary engine to monitor engine output and pump rate.
Is anyone using this combination?

Thanks.

431
1
laurabacani posted Mar 3 '21 at 7:53 pm
Dear all,
We have had problem with our Datataker DT80 since New Year, and we have been trying to fix that for two months now, but unsuccessfully.
So I am writing to you in hope somebody could help us.
The problem have begun when Adobe Flash stopped working on December 31, 2020. Since then, we haven't managed to connect with our logger DT80. We have installed dex 2.0, as it is instructed
69
3
Beshoy Kameel posted Feb 22 '21 at 12:50 pm
Hi,

I had installed a DT85 series 4, then changed the memory from 128MB to 2GB, and started up the datataker.
After starting up the LCD shifted its messages to the right of the display tell only half of the massege was shown (for example ethernet IP was 192.168.8.100 but 192.168 only appears)

I made a hard reset and "Reset" command, but after the reset the display keeps shifting again
42
3
ganeshraj26 posted Mar 1 '21 at 5:11 am
Good Day Everyone,
I am facing problem with applying program to logger since the power always changes from setted 'always' to 'only when taking reading' which causes our equipment to not function accordingly.



603c76cdc4ccd
54
2
We'd like to use the software Desktop dEX in our company, but as we need it to be installed on around 50 clients we're looking for a possibility to automate installation so no user interaction is necessary.
I didn't find anything online regarding this topic and there were no parameters shown when I tried to start the setup from the commandline with /help or /?.
I'm really looking forward to